M600 SEK fault

member 18943

Previous User
Joined
2017
Posts
0
Was any one face the error message #140 SEK no run
M600 GOSS press
IMG-20210128-WA0002.jpeg
 
Dear maher
This message happen when there is redundant contact of safety guards, units crank, emergency stop give wrong signal and red lamps in console is on
Remdy
1 check sek status and check which number is highlighted then you can find the wrong push button
2 check the SEK and swap it the SEK card on post unit
3 sek may be not engaged
4 check the fem10 1 to
It should 24 V dc
 
  • Dear maher
    1 Are you swap sek with sek on post unit
    2 Check the engage sek with motherbord
    3 check the plugs for sek in the back of the motherboard
    4 the image u send for sek1
    Check sek2 also if there is highlighted or not
    Send your whatsapp
     
    Dear maher
    Check all contact for all emergency stop
    Each stop has to points one for eak and one for sek
    Check one by one
    May there cut in cable from fem 64 to eak
    Or bad eak change them by one from post
    Send your whatsapp to be more simple in communication
     
    Dear maher
    Check all contact for all emergency stop
    Each stop has to points one for eak and one for sek
    Check one by one
    May there cut in cable from fem 64 to eak
    Or bad eak change them by one from post
    Send your whatsapp to be more simple in communication
    Dear maher
    Did you solve the problem?
     
    If stop buttons check out to being okay then it could be a bad guard switch. Had this happen many a time. Water especially from when a rotary union goes bad gets into the guard switches and shorts them out. If you bring up the SEK screen when this happens you can open and shut guards and watch the 0 and 1 change. Basically you open guards until one doesn't respond to a change and then you know which guard switch is bad.
     
    If stop buttons check out to being okay then it could be a bad guard switch. Had this happen many a time. Water especially from when a rotary union goes bad gets into the guard switches and shorts them out. If you bring up the SEK screen when this happens you can open and shut guards and watch the 0 and 1 change. Basically you open guards until one doesn't respond to a change and then you know which guard switch is bad.
    Thanks for your reply
    We found the stop
     
  • Hi sir....same error ....141 no run sek, m600 cptronic... need hlep
     

    Attachments

    • 20220630_161629.jpg
      20220630_161629.jpg
      148.8 KB · Views: 346
    • 20220630_161646.jpg
      20220630_161646.jpg
      155 KB · Views: 367
    • 20220630_161541.jpg
      20220630_161541.jpg
      209.3 KB · Views: 350
    • 20220630_161603.jpg
      20220630_161603.jpg
      246.1 KB · Views: 346
    Thanks all....
    My machine SEK error problem shortcut....
    Thanks to all.....
     
    Forum posts represent the experience, opinion, and view of individual users. The Color Printing Forum does not necessarily endorse nor share the view of each individual post. When making any potentially dangerous or financial decision, always employ and consult appropriate professionals. Your circumstances or experience may be different.