Technotrans

Discussion in 'DI Presses' started by Marc Bremer, Jan 13, 2011.

  1. Marc Bremer

    Marc Bremer Senior Member

    Joined:
    Jan 2010
    Messages:
    239
    Location:
    Netherlands
    Moved the technotrans away from the catwalk to another room, when the initial setting is reached (23 degrees) the blower on the technotrans start to run and will stay on constantly, I can't remember if he did this when it was installed under the catwalk (I thought he switched off now and than).
     
  2. Paul Cavanaugh

    Paul Cavanaugh Senior Member

    Joined:
    Dec 2009
    Messages:
    630
    Location:
    Kennesaw, GA
    It should come on and off based on whether it is cooling or not. Have you cleaned the condensor on it? Sometimes this gets clogged up with powder and paper dust and will cause the unit to run continuously.
     
  3. Marc Bremer

    Marc Bremer Senior Member

    Joined:
    Jan 2010
    Messages:
    239
    Location:
    Netherlands
    The condensor I cleaned when I removed it, then fan and compressor or off when I switch on the machine temperature rises and 0.5 degrees below setpoint (23 degrees) compressor and fan start to run and keep running. I hear a valve switching when the temperature rises 0.2 degrees above setpoint. If I change setpoint to 24 degrees compressor and fan switch of.
     