Man Roland 700 UWR problem

James07

Member
Joined
2018
Posts
7
Geo
Antalya turkey
Man Roland 700 1995

the machine is warming up in the afternoon antalya very hot 35- 36 C
this error occurs when clicking the start button

UxXCkWjV2C
 

Attachments

  • 20220720_175023.jpg
    20220720_175023.jpg
    287.3 KB · Views: 835
  • yes 4 - 5 months
    I checked the switch, it works normally but the problem is not solved
     
    1. check the motor encoder/tacho
    2. is there any error with the main drive unit?
     
    yes 4 - 5 months
    I checked the switch, it works normally but the problem is not solved
    The switch works, ....the input says the same?
     
    Hi
    We have the same problem with UWR but only when i start from delivery side.
    IMG_20220912_140421.jpg
    When i start from feeder side its all ok.
    I have checked the Brake switch - all ok.
    How can i solve this problem?
    Thanks
     
    I still could not solve the problem, especially after the machine warms up.
     
    Hi
    We have the same problem with UWR but only when i start from delivery side.
    View attachment 11784
    When i start from feeder side its all ok.
    I have checked the Brake switch - all ok.
    How can i solve this problem?
    Thanks
    hello
    08: not ready for operation, i.e. terminal 19 =“0“ (EMERGENCY OFF is activated)
    probably the input board at delivery station is defective. you must check slot 3,4 (input boards) and slot 2 (safety relay board UWR)
     
    Thanks.
    But I have done those checking. (no results)
    I'll try to change the Tachogenerator.
    This is something I haven't done before
     
    you said if you start from the feeder panel it's all ok and only have a problem from the delivery side. then it's not the tachogenerator I think you should check the delivery station again.
     
    When the problem is present only at one station panel control then is a problem with station safety bus, or maybe is just the board where the run commands are mounted this is easy to check just interchange the control panel board with other station
     
  • safety relay board slot 2 in the delivery station and the board where the run commands are mounted.
     
    I tried to change all the boards with other station. But I didn't get the result (((((
    May be the cable ?
     
    Forum posts represent the experience, opinion, and view of individual users. The Color Printing Forum does not necessarily endorse nor share the view of each individual post. When making any potentially dangerous or financial decision, always employ and consult appropriate professionals. Your circumstances or experience may be different.